Переодически отваливается UPS Ippon Back Power Pro 500

Post by surock »

Добрый день!
Помогите разобраться в чем проблема!
Установлена ось Nas4Free 10.2.0.2 - Prester (сборка 1906). NAS подключен к электросети через Ippon Back Power Pro 500 и соединен с ним USB шнурком из комплекта поставки ИБП. Переодически отваливается ИБП:

Code: Select all

upsd[1752]: Can't connect to UPS [UPS] (blazer_usb-UPS): No such file or directory
upsmon[1790]: Poll UPS [UPS@localhost] failed - Driver not connected
last message repeated 7 times
last message repeated 16 times
upsmon[1790]: UPS UPS@localhost is unavailable
upssched-cmd: UPS UPS@localhost - The ups is unavailable
upsmon[1790]: Poll UPS [UPS@localhost] failed - Driver not connected
Настройки
Image

Пробовал менять драйвера - blazer_usb, blazer_usb protocol=megatec. ИБП отваливался раз в час. После установки дополнительного параметра pollinterval=15 ИБП стал отваливаться раз в сутки.

Что можно сделать? Где искать решение?
11.2.0.4 - Omnius (rev. 6766)
Asus AT5NM10T-I, 4Gb RAM, SSD KingDian 16GB (system + SWAP), 2 x HDD Seagate ST4000VN000 4Tb (zfs mirror), APC Back-UPS CS 500.

User avatar
MikeMac
Forum Moderator
Forum Moderator
Posts: 429
Joined: 07 Oct 2012 23:12
Location: Moscow, Russia
Contact:
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by MikeMac »

surock wrote:blazer_usb-UPS
Старая проблема с драйвером, ср viewtopic.php?f=46&t=946

Люди рекомендуют
pollinterval=10
(а не 15) Но всё равно отваливается. В конце упомянутой ветки есть скрипт, который рестартует nut при нужде.

А в ветке https://forums.freenas.org/index.php?th ... ups.17192/
пишут, что достаточно рестартовать сам драйвер (пост от Jan 29, 2014 и ниже)


Думаю, если отваливается раз-два в сутки решение с рестартом сойдёт. А в целом - выбор UPS под nix - не простое дело. Совместимость зависит от того, насколько производитель публикует протокол. Вот APC опубликовал полностью и проблем - минимум.

sergey1878
NewUser
NewUser
Posts: 14
Joined: 18 Oct 2015 09:32
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by sergey1878 »

У меня Ippon Smart Power Pro 2000. Работает с nas4free 10.2 без проблем вообще. Драйвер такой-же как и у автора. Видимо дело в модели упса

surock
NewUser
NewUser
Posts: 7
Joined: 23 Oct 2015 10:35
Location: Russia, Moscow
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by surock »

Всем доброе время суток.
Решил я проблему периодической отвалки UPS Ippon Back Power Pro 500. Спасибо MikeMac за помощь...! Необходимо установить скрипт перезапуска самого драйвера blazer_usb в случае потери связи NAS сервера с UPS-ом.
И так, более подробно:
1. Начинка NAS: ASUS P5B-VM SE, Intel Pentium D CPU 3.00GHz, 2Gb=4х512Mb PC2-6400 (800 МГц), zfs mirror 2x1Tb WD Caviar Green WDC WD10EZRX-00D8PB0, ufs stripe (system + swap + data) 160 Gb Seagate Barracuda 7200.10 ST3160815AS, DVD-RW.
2. Установленная ОС: Nas4Free 10.2.0.2 - Prester (сборка 1906) x64-full.
3. Блок бесперебойного питания: UPS Ippon Back Power Pro 500 USB.
4. Настройки службы UPS
Службы | UPS
Image
Драйвер: blazer_usb
Дополнительный параметр: pollinterval=10
5. У меня установлена полная версия Nas4free на жесткий диск, поэтому пупку со скриптом (/ups/ups_script.sh) я решил поместить в корень системного диска. Все махинации с созданием папки и файла скрипта делал при помощи PuTTy через SSH.
6. Сам скрипт:

Code: Select all

#!/bin/bash
if [[ $(/usr/local/bin/upsc ups | grep 'device.type') == *ups ]]; then
exit 0
else
/usr/local/libexec/nut/blazer_usb -a ups
fi
7. Добавил в cron и перезагрузил
Image

ИТОГ: Больше ошибка не появляется! Работает 24/7. Тест на отключение электричества NAS прошел, через минуту с копейками отключился.
11.2.0.4 - Omnius (rev. 6766)
Asus AT5NM10T-I, 4Gb RAM, SSD KingDian 16GB (system + SWAP), 2 x HDD Seagate ST4000VN000 4Tb (zfs mirror), APC Back-UPS CS 500.

surock
NewUser
NewUser
Posts: 7
Joined: 23 Oct 2015 10:35
Location: Russia, Moscow
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by surock »

Отчет о работе выше упомянутого метода решения проблемы периодической потери связи сервера с UPS Ippon Back Power Pro 500!

Слышал два сигнала динамика ПК с разницей в несколько секунд. В журнале появилась запись:

Code: Select all

Feb 16 12:10:34 	nas 	blazer_usb[1767]: Permissions problem: Input/output error
Feb 16 12:10:34 	nas 	upsd[1769]: Can't connect to UPS [ups] (blazer_usb-ups): No such file or directory
Feb 16 12:10:36 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 12:10:36 	nas 	upsmon[1807]: Communications with UPS ups@localhost lost
Feb 16 12:10:36 	nas 	upssched-cmd: Communications with the UPS ups@localhost are lost
Feb 16 12:10:41 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 12:11:01 	nas 	last message repeated 4 times
Feb 16 12:11:06 	nas 	upsmon[1807]: Communications with UPS ups@localhost established
Feb 16 12:11:06 	nas 	upssched-cmd: Communications with the UPS ups@localhost are established
Так что все работает! Связь была потеряна и тут же восстановлена!
11.2.0.4 - Omnius (rev. 6766)
Asus AT5NM10T-I, 4Gb RAM, SSD KingDian 16GB (system + SWAP), 2 x HDD Seagate ST4000VN000 4Tb (zfs mirror), APC Back-UPS CS 500.

User avatar
alexey123
Moderator
Moderator
Posts: 1469
Joined: 19 Aug 2012 08:22
Location: Israel, Karmiel
Contact:
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by alexey123 »

Два подобных упса, и ничо так, оба нормально работают.
Home12.1.0.4 - Ingva (revision 7091)/ x64-embedded on AMD A8-7600 Radeon R7 A88XM-PLUS/ 16G RAM / UPS Ippon Back Power Pro 600
Lab 12.1.0.4 - Ingva (revision 7091) /x64-embedded on Intel(R) Core(TM) i3-3220 CPU @ 3.30GHz / H61M-DS2 / 4G RAM / UPS Ippon Back Power Pro 600

surock
NewUser
NewUser
Posts: 7
Joined: 23 Oct 2015 10:35
Location: Russia, Moscow
Status: Offline

Re: Переодически отваливается UPS Ippon Back Power Pro 500

Post by surock »

Вот такая картина нарисовалась за сутки:

Code: Select all

Feb 16 12:10:34 	nas 	blazer_usb[1767]: Permissions problem: Input/output error
Feb 16 12:10:34 	nas 	upsd[1769]: Can't connect to UPS [ups] (blazer_usb-ups): No such file or directory
Feb 16 12:10:36 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 12:10:36 	nas 	upsmon[1807]: Communications with UPS ups@localhost lost
Feb 16 12:10:36 	nas 	upssched-cmd: Communications with the UPS ups@localhost are lost
Feb 16 12:10:41 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 12:11:01 	nas 	last message repeated 4 times
Feb 16 12:11:06 	nas 	upsmon[1807]: Communications with UPS ups@localhost established
Feb 16 12:11:06 	nas 	upssched-cmd: Communications with the UPS ups@localhost are established
Feb 16 19:38:37 	nas 	blazer_usb[3497]: Permissions problem: Input/output error
Feb 16 19:38:37 	nas 	upsd[1769]: Can't connect to UPS [ups] (blazer_usb-ups): No such file or directory
Feb 16 19:38:40 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 19:38:40 	nas 	upsmon[1807]: Communications with UPS ups@localhost lost
Feb 16 19:38:40 	nas 	upssched-cmd: Communications with the UPS ups@localhost are lost
Feb 16 19:38:45 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 16 19:39:00 	nas 	last message repeated 3 times
Feb 16 19:39:05 	nas 	upsmon[1807]: Communications with UPS ups@localhost established
Feb 16 19:39:05 	nas 	upssched-cmd: Communications with the UPS ups@localhost are established
Feb 17 10:29:03 	nas 	blazer_usb[7047]: Permissions problem: Input/output error
Feb 17 10:29:03 	nas 	upsd[1769]: Can't connect to UPS [ups] (blazer_usb-ups): No such file or directory
Feb 17 10:29:07 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 17 10:29:07 	nas 	upsmon[1807]: Communications with UPS ups@localhost lost
Feb 17 10:29:07 	nas 	upssched-cmd: Communications with the UPS ups@localhost are lost
Feb 17 10:29:12 	nas 	upsmon[1807]: Poll UPS [ups@localhost] failed - Driver not connected
Feb 17 10:29:47 	nas 	last message repeated 7 times
Feb 17 10:29:57 	nas 	last message repeated 2 times
Feb 17 10:30:02 	nas 	upsmon[1807]: Communications with UPS ups@localhost established
Feb 17 10:30:02 	nas 	upssched-cmd: Communications with the UPS ups@localhost are established
Характеристики железа и ОС: ASUS P5B-VM SE, Intel Pentium D CPU 3.00GHz, 2Gb=4х512Mb PC2-6400 (800 МГц), zfs mirror 2x1Tb WD Caviar Green WDC WD10EZRX-00D8PB0, ufs stripe (system + swap + data) 160 Gb Seagate Barracuda 7200.10 ST3160815AS, DVD-RW, UPS Ippon Back Power Pro 500 USB, Nas4Free 10.2.0.2.1906 x64-full.

Возможно это особенности именно этого упса. На праздниках попробую сделать тоже самое на домашнем серваке: Asus at5nm10t-i с процессором Intel Atom D525 1,8 GHz, 4Gb ОЗУ (2х2Gb DDR2 800 МГц 6400 МБ/с), LAN 10/100/1000 Base-T, zfs mirror 2х4Gb Seagate NAS HDD SATA3 ST4000VN000, ufs stripe 640 Gb 2.5" HDD SATA2 (8Gb system + 4Gb swap + data), UPS Ippon Back Power Pro 500 USB, Nas4free 10.2.0.2.2268 x64 full.

И позже отпишусь!
11.2.0.4 - Omnius (rev. 6766)
Asus AT5NM10T-I, 4Gb RAM, SSD KingDian 16GB (system + SWAP), 2 x HDD Seagate ST4000VN000 4Tb (zfs mirror), APC Back-UPS CS 500.